Menu Submenu Indication
Information
Test of device
Safety test
Setting Code insert
---
Set the code by „+“ button. Random
number lights on the left side. Insert code
and confirm by „←“ button. Technician´s
number is available from supplier of the
boiler.
01 :Language
German DE
English GB
Italian IT
French FR
Swedish SE
Polish PL
Slovak SK
Czech CZ
Dutch NL
Danish DK
Hungarian HU
Slovenian SI
Function: Setting of national language
02 : Setting of boiler
°C 85
Function: Set boiler temperature
Producer: 85°C
Range of setting: 75°C – 85°C
03 : Setting of TAG
°C 180
Function: After setting of flue gas
temperature (nominal 180°C boiler output).
Producer: 180°C
Range of setting: 110°C up to 240°C
Tip: TAG = flue gas temperature
04 : Setting of O2
% 6,0
Function: Setting of O2 value for
combustion 6 %
Producer 6,0 %
Range of setting: 4,0 % up to 8,0 %
05 : Start TAD
K 60
Function: to reach sufficient output before
the feeding door is closed
Producer: 60K
Range of setting: 25K up to125K
21
Tip: TAD= temperature difference. It is
a difference between flue gas temperature
and temperature in the boilers
06 : Disconnection
O2
TAG
Function: Boiler for wood combustion is
switched off in consequence of:
O2 – indicates higher level of coal residual.
(easier start)
TAG – indicates minimum coal residual
(recommended by combustion problems –
deformed or wet fuel)
Producer: O2
Setting: O2/TAG
10 : V1 Primary air
Air (%) 85
Function: By flue gas sensor error or
oxygen sensor error it regulates adjusted
temperature. It serves as temporary
solution, until the error is removed - it is
not a standard operation function in any
case!
Producer: 85 %
Range of setting: 0 % - 100 %
11 : V2 Secondary air
Air (%) 40
Function: By flue gas sensor error or
oxygen sensor error it regulates adjusted
temperature. It serves as temporary
solution, until the error is removed - it is
not a standard operation function in